Run a higher voltage closer to the service entrance location, set a transformer, utilize nothing bigger then 500KCMIL off the LV side of the transformer.
chaterpilar said:Two smaller conductors will produce more heat than one bigger conductor of equivalent cross-sectional area.
as per Table 310.15(B) .2 the effect is pronounced only if number of conductors are more than 3 per conduit.
Bob what are the two breakers for are there Alternate feeds to this xformer ?? And if there is are they locked out with some of key arangement so both feeds cannot be on at the same time.??iwire said:That is news to me and I work with them. :smile:
Here is a transformer before we installed the 600s.
It is roughly 4' W x 5' H
Here it is after.
It was not easy getting all that in and I had a lot of room between the terminals and the bottom.
Actually, both frequency and current are factors. The higher the frequency, the less the current has to be for a given size conductor for skin effect to become significant.chaterpilar said:I thought "skin effect" comes into play only at high frequencies and is negligible at 60 Hz.
quogueelectric said:Bob what are the two breakers for are there Alternate feeds to this xformer ??
iwire said:GE calls it a "transformore" or something like that, they say it is a benefit to the customer because it is smaller, I think it is just cheaper to make. :roll:
Whatever you choose, DO NOT get 900 kcmil compact aluminum, we've had nothing but trouble with it.rconteng said:I am wondering whether it will make a difference to a contractor if he were asked to pull five parallel runs of 4 conductor 1000 kcmil cable in 5" conduits vs 6 runs of 4 conductor 750 kcmil in 4" conduits. The distance is roughly 600 feet.
chaterpilar said:Nateholt,
For example
10 Awg is half the size( diameter) of 4 Awg and ..assuming we use 1 run of 4 Awg instead of 2 runs of 10 Awg,
chaterpilar said:10Awg = 0.00319 ohms/meter
4 Awg = 0.000793 ohms/meter
so for 1 meter length and 10 amps current
4Awg
Watt loss = I*I*R = 10*10*0.000793= 79 miliwatts
10Awg
Watt loss = ( 5*5*0.00319) * 2 = 159 milliwatts.
More watt loss means more heat.
Cheers.
cadpoint said:Iwire,
What is the set bolt used in the multi-lug assemblies, is a special tool required ? It looks like two eye-lets at the end of each lug/bolt?
It also looks like a ceramic block on the underside the breakers?
But in re-examining the photo the aluminum lugs are used on top, it must be the angle and such of the picture!
iwire said:As an installer I would rather limit it to no larger then 600 Kcmil unless the enclosures have a lot of space.
nakulak said:Hey Bob, not trying to bust your chops, but didn't you exceed the bending raduis on those conductors ?
chaterpilar said:i stand corrected,..but still it is more....and multiply it by 200 metres, and remember this loss will be forever....(lifetime of the equipment)