1000 KVA Transformer wire size

Merry Christmas
Status
Not open for further replies.

Joshb

Member
Location
Charlotte, NC
Can anyone help me with figuring the wire size on the primary feed for a 13,800V primary feed to a transformer. The power company was going to install but that has changed and now we are installing the primary feed and the transformers. The transformers are 1000 KVA. What calculation should I use for this?

Thanks
 
Can anyone help me with figuring the wire size on the primary feed for a 13,800V primary feed to a transformer. The power company was going to install but that has changed and now we are installing the primary feed and the transformers. The transformers are 1000 KVA. What calculation should I use for this?

Thanks

I suspect it will end up being the smallest wire you can find suitable for the voltage.
 
The calculation I used was 1000 x 1000 / 13800 x 1.73 = 42A? Doesnt seem right though...
That part is right. But we can size a breaker up to 4 times that value, or a fuse up to 3 times that value. The minimum size per the table cited by xformer is #2, and that will have sufficient ampacity for even 4 times 42 amps.
 
Overhead feed or U.G.
Our POCO uses 1/0 for underground up to 2000 kva.
 
Overhead feed or U.G.
Our POCO uses 1/0 for underground up to 2000 kva.


It's an U.G. feed. There are 3 transformers (2) 1,000 kva's and (1) 750 kva. I now have added up all the loads for a total
of 2,750 kva. New calculation - 2,750 x 1000 / 13,800 x 1.73 = 115A
 
Take a look at 450.3(A) decide what primary OCP is correct and size accordingly.
 
It's an U.G. feed. There are 3 transformers (2) 1,000 kva's and (1) 750 kva. I now have added up all the loads for a total
of 2,750 kva. New calculation - 2,750 x 1000 / 13,800 x 1.73 = 115A

A diagram would be helpful. Make one and then try to calculate.
 
There are 3 steps in order to design a medium voltage cable:
1) short-circuit current withstand
2) ampacity [allowable current-carrying capacity]
3) Voltage drop [mainly if a large induction motor will start D.O.L or Wye- Delta].
1) Usually for 13.8 kV the average rms short-circuit current will be 30 kA and the protection clearance time could be -close 0.1 sec and reserve 0.5 sec. For 30 kA and 0.5 sec fault clearance time, copper conductor, XLPE insulation [250 dgr.C short-time temperature limit] 300 kcmil [150 sqr.mm] will be suitable.
2) Ampacity could be stated from NEC art. 310. Let's say the cable will run in earth at 90 RHO -thermal resistance 20 dgr.C. Transformer rated current will be 1000/13.8/sqrt(3)=41.84 A.
According to Table 450.3(A) Maximum Rating or Setting of Overcurrent Protection for Transformers for less than 6% transformer rated impedance overcurrent protection required is 600% transformer rated [6*41.84=251 A].
Art.240.4 Protection of Conductors: overcurrent protection shall not be more than feeder ampacity[for less than 800 A could be a little more in certain conditions]
According to NEC Art.310 Table 310.60(C)(83) Conductors Cabled Within an Overall Covering (Three-Conductor Cable), Directly Buried in Earth. For Detail 5[one cable] 5001-35000 V 250 kcmil copper conductor 90oC insulation rated ampacity is 380 A.
 