Phil Timmons
Senior Member
- Location
- DFW
- Occupation
- Depends on the pay and the day
Of course there’s a DC disconnect at the SMA TriPower inverter, just not physically exiting the array itself.
Yeah, that pushes things into needing to move the Inverter right up to the array, at least for Rooftop installs.
But since you are ground mount, maybe you can install the SMA at or near the array? Otherwise you are bringing the DC runs to (where?) (a building?) -- you know you cannot bring that DC inside the building, right? Without the rapid shutdown, I mean. But I see folks doing that. Bringing the DC inside I mean - wiping out the entire advantage of having not put the Solar on the roof.
Other thing have noticed with SMA is that by putting the On/Off for AC and DC on opposite sides -- we now have inspectors calling for Working Space (Art 110) on BOTH sides of the inverter, along with wanting us to put protection over/around the exposed DC 1000V cables that enter on the back. mho -- SMA should be revisiting the ENTIRE design of this thing.