To clarify a bit more, here is a portion of the response from a cable engineer:
... 690.31 states that ?All raceways and cable wiring methods included in this Code and other wiring systems and fittings specifically intended and identified for use on photovoltaic arrays shall be permitted? .... Nowhere in Article 690 are underground installations specifically mentioned.
Neither the language in 690 or 300.50 is perfectly clear. However, based on the language in 690.31, my position is that since our PV conductors are Listed for and ??specifically intended for use on photovoltaic arrays?? our customers should be able to direct bury the single conductors, even when the nominal system voltage is over 600 volts."
However, based on the language in 690.31, my position is that since our PV conductors are Listed for and ??specifically intended for use on photovoltaic arrays?? our customers should be able to direct bury the single conductors..."
I am in agreement with you. I contend that the intent of 300.50 is personnel protection, should someone come into contact with the cable. The grounded metal sheath would provide a return path. Direct buried cables that are not protected with a ground return path are not in compliance. This is why PVC in earth would not be acceptable as well.
By following the NEC 2014, 310.10(F) and 300.5, can we install a 2kV PV (PV and RHW-2) wire (Circuit voltage is 1000V) in a PVC/IMC/RMC raceway 24" below grade? Can it also be directly buried 24" below grade? Or is there any other code that I have t follow? Thanks