Augie47 I see you are a retired TN electrical inspector and I am a retired TN State Trooper Lieutenant. I will look into the internal fusing, but
NEC 424.3 (A) also states: Individual branch circuits shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which they are rated. Does this cover my 80 Amp Circuit since this is the only thing on this circuit?
"I calculated the CB as 14,400/240 = 60A x 1.25 = 75A so I am using an 80A breaker."
NEC 424.3 (A) also states: Individual branch circuits shall be permitted to supply any volt-ampere or wattage rating of fixed electric space-heating equipment for which they are rated. Does this cover my 80 Amp Circuit since this is the only thing on this circuit?
"I calculated the CB as 14,400/240 = 60A x 1.25 = 75A so I am using an 80A breaker."