That section only says that you don't have to size the EGC for motor circuits to the rating of the branch circuit ground fault and short circuit protective device if that device is an instantaneous trip circuit breaker or a motor short-circuit protector. If that is the case then you can size the EGC based on the rating of the motor overload device. If the branch circuit OCPD is a fuse, or thermal magnetic breaker, then the EGC must be sized based on the rating of the branch circuit OCPD.danickstr said:If it was oversized for a motor, then the 12 g is OK
250.122 d
Don