Is it allowed by code in a residential setting with a 200A panelboard to measure the required 30" from the right side of the panelboard edge facing you and be 30" from the wall to the left of the panelboard?
 
Re: 110.16(A)

I'm not sure that I understand your question. Sounds like you're asking does the panel have to located in the center of the 30" dimension or can it be 30" from the panel edge to the wall. Is this correct?
 
Re: 110.16(A)

There has to be 30 inches of clear space. The panel can be at the left edge of that 30 inches, or at the right edge, or anywhere in the middle. The only requirement is that the entire width of the panel must be clear, and that enough extra space must be clear on the left and/or the right side to get a total of 30 inches.
 
Re: 110.16(A)

..maybe if you checked 110.26 it would be clearer :)

See 110.26(A)(2) Width of Working Space.
 