I need clarification from the experts here.
An inspector turned down an electrical room for violation of working space.
He says the switchboards have live parts on each front side so this would be condition 3 of Table 110.26(A)(1). (They are both serviced from the front)
I never thought about this until this came up.
My first thought would be; If I only work on one switchboard at a time, you would be under condition 2 because you would have live parts on one side and grounded parts on the other. This would put me in condition 2 as opposed to condition 3 which now is the violation.
What do the experts say here based on their interpretation of the intent of the code?