I have a scenario where two (2) 1200A, 120/208V distribution panels will be installed in a room with only one entrance/exit. The panels are over 6ft wide and will be installed with their fronts facing each other, creating a single working space between them. The setup is identical to exhibit 110.22 of the 2017 NEC Handbook.
It's clear from 110.26(C)(2)(b) that in this scenario, the required working space between the panels in this example is 6ft and that the entrance shall be located such that the distance between equipment to the nearest edge is not less than 3ft. Sketch 'a' is a proposed dimensioned equipment and room layout using exhibit 110.22 as a basis of design.
Referring to sketch 'b' attached, my question is - would the use of double doors instead of a single door be in compliance of the 3ft lateral clearance required for the room entrance since 1 of the 2 doors will always be outside of the "working space" of each distribution panel? Or is the double doors still technically considered a "single entrance" since they are in the same location at one end of the aisle? The goal is to keep the footprint of this room as small as possible, so if code compliant, sketch 'B' will allow for a slight reduction of the room dimensions. TIA!
sketch 'a'
sketch 'b'
It's clear from 110.26(C)(2)(b) that in this scenario, the required working space between the panels in this example is 6ft and that the entrance shall be located such that the distance between equipment to the nearest edge is not less than 3ft. Sketch 'a' is a proposed dimensioned equipment and room layout using exhibit 110.22 as a basis of design.
Referring to sketch 'b' attached, my question is - would the use of double doors instead of a single door be in compliance of the 3ft lateral clearance required for the room entrance since 1 of the 2 doors will always be outside of the "working space" of each distribution panel? Or is the double doors still technically considered a "single entrance" since they are in the same location at one end of the aisle? The goal is to keep the footprint of this room as small as possible, so if code compliant, sketch 'B' will allow for a slight reduction of the room dimensions. TIA!