Moosifer
Member
- Location
- Panama City Beach, FL
Any thoughts on this? I'm waiting to find out where the shower head is if there is one. Just got asked if this was legal by a customer. I'm scared it might be ok if there is no shower head above.View attachment 23047
Does not violate anything code wise. That said, I would not be inclined to do it if given the choice due to future maintenance issues.
I didn't put it there and wouldn't put it there. A disaster recovery contractor that we do work for asked if it was to code since it is in a house they are working on an hour away from here. I don't think it is to code or should be but I can't find anything saying that it isn't.
That was my feeling but then I read 110.26(E) and although I always thought it referred to surface mounted panels it does not say that so why would plumbing be allowed above this panel... assuming there is a shower head in the same bay as the panel.
The piping cannot be in the dedicated equipment space which is equal to the width and depth of the panel.
View attachment 23049
I interpret the dedicated space as "working space", to safely work on the equipment, not about keeping water from a leak going on it. You could have plumbing on the floor above, a toilet or washing machine. The code allows sprinkler pipes in the space, which could burst and leak. Once they sheet rock is there any clearance issue then? How many panels have you swapped out where the plumbing in the ceiling joists is almost over your existing panel?
It does also say condensation and leaks, and as Dennis said it doesn't address a flush mount installation. Maybe OP should ask the inspector, if it's an insurance job he probably needs a permit.There are two different things. Working space is in front of the equipment, dedicated equipment space is directly above and below the equipment.
It does also say condensation and leaks, and as Dennis said it doesn't address a flush mount installation. Maybe OP should ask the inspector, if it's an insurance job he probably needs a permit.
Where does it say the requirement is only for surface mounted installations?