110.26 Question

Status
Not open for further replies.

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
Let's be real
not a problem Denny

i want my 'space' , i tell all my clients and GC's i want to be able to walk up to my panel(s) , keep all other trades out

A 3x3 area should not be too much to ask for , especially considering all the other trades wanting far more space than we desire

also, and even of more relevance , my work is art , or maybe 'lectrical porn is a better term for my peers

h*ll, after 4 decades i've earned it!

Up the regiment!
💪
~RJ~
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That is correct. The pipe is not directly over the panel. It's probably 2" out of the panel footprint.
Then there is no issue. The pipe is not within the dedicated equipment space and is above the 6'6" minimum height for the working space.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I had a job a couple of years ago where the plumbing was put in after my panels in the basement. The main drain line, like the OP, was right over my panels. Inspector made them put a drip pan under the pipe in order to not have to move the pipe. Had I not already wired the panels, I would have had them move it because it would have been very difficult to get the wires in with that pipe in the way.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is it hurting anybody? Is it ever likely to get in the way of somebody working on the equipment? Since the answer to both of these questions is no, what is the purpose of the rule in this case other than an arbitrary rule that just gives inspector something to nitpick about.
"Code is code
We don't like the rules we don't agree with
Its ok for someone else
But not if it costs us time and money"
Mike Holt
 