cripple
- Santa Fe, New Mexico
I would like for soon one to clarify the working clearances requirements for fusible and non-fusible disconnects, especially the height of the working space per 110.26(A)(3).
110.26 requires sufficient access and working space to be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
110.26(A) clearly state the requirements for equipment likely to require examination, adjustment, servicing, or maintenance while energize, and (1) requires the depth of the working space not to be less than that specified in Table 110.26(A)(1) unless the requirements of 110.26(A)(1)(a), (A)(1)(b), or (A)(1)(c) are met.
110.26(A)(3) requires the height of the working space to be clear and extend from the grade, floor, or platform to the height required by 110.26(E). But when I go to 11026.(E) the minimum headroom of working space is only required for service equipment, switchboards, panelboards, or motor control centers. Does this mean that the headroom is not required control panel, starter, and disconnecting means?
