It's probably staring me in the face but I'll ask anyways...
Which working clearance article is the 1st pic violating 480?
Combination of 110.26(A)3 and 110.26(A)1
See the step thingy at the bottom .....
Watch your step.
![]()
![]()
______________
Watch your step.
![]()
Rob
Maybe the picture does not show enough...what is the issue here?
Do those conductors on the right violate 312.6?
No. Conductors can never violate that section, as it applies to the equipment the condcutors are in, and not the conductors themselves. The equipment appears to be about 6" in depth (give or take), so you could legally install 500 kcmil conductors without the equipment being noncompliant.