Does a disconnect switch require working space? In other words, does it fall under Article 110.26A as an equipment likely to require examination, adjustment, servicing or maintenance while energized?
Does a disconnect switch require working space? In other words, does it fall under Article 110.26A as an equipment likely to require examination, adjustment, servicing or maintenance while energized?
Everything out there can de- energized as well, so why even bother with the "likely to be energized" portion? Some items may not be as simple as others to de- energize but is still possible.The likely to be energized is another clue -- can you turn off the OCPD to the branch circuit? And if so is the OCPD readily accessible? Just because an electrician chooses to work on live wiring does not mean it is likely to be energized. Every circumstance might dictate a different answer. As for you question with a non fused disconnect normally no.
Everything out there can de- energized as well, so why even bother with the "likely to be energized" portion? Some items may not be as simple as others to de- energize but is still possible.
You are required to do so per 70E and OSHA.you do not turn off the entire power panel to change a breaker ...
You kind of missed my point yet hit on some more examples that I may have given.you do not turn off the entire power panel to change a breaker "likely to be energized" an exterior disconnect for an appliance might be fed from an interior panel behind locked doors rendering the OCPD non readily accessible "likely to be energized" I would interprete the "likely to be enrgized" is entered as all circumstances cannot be anticipated and judgement calls are required. Anyone could summize most electricians work on devices & j boxes that are energized more than 50% of the time. should we now require working space for kitchen countertop recepts? The code allows judgement calls for "likely to be enrgized" which is why we bother.
You are required to do so per 70E and OSHA.
...
I was trying to say - what is the point of NEC saying "likely to be energized" - when most AHJ's look at it as everything "can be energized" when someone is working on it. It is possible to open the supply on anything that gets worked on, even service gear - doesn't mean it always happens or is deemed practical. ...
You are leaving out a key word in the rule. This really goes to my point as to the meaning of the word "required" as used in this section.( A) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.