raider1 said:110.26(A)
110.26(A) doesn't require a piece of equipment to have "serviceable parts" to need the required working space.
Read the section "Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the diminsions of 110.26(A)(1), (A)(2), and (A)(3)..."
How do you check for voltage without the disconnect being energized?
Again I don't think that fuses are required for a disconnect to need to meet the requirements of 110.26(A)
Chris
So my question again is does a breaker lock solve anything.He still needs to work on it live.We can simply turn off the main breaker to solve this.Actually that is an idea because my main is outside in sight.Does nec say i cant kill everything to meet this requirement ?