Would like to get the opinion of the forum on an issue that came up the other day concerning the following article:
(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
I installed a panel under a house with a dirt floor basement using the exception to this article. The ceiling height varied from 6 1/2 feet to 4 feet at different areas. The hot water heater, well pump, furnace, were all installed in this area. The original location of the panel was behind a kitchen cabinet and no longer could be installed in the same location. My options were to install it out doors or in the basement. I choose the basement. The height was about 4 1/2 feet at the edge of the basement wall. I was told by the electrical inspector that it was not the intent of the code to install a panel in this location unless there was already a panel in that spot. I resolved the issue by digging a 2 foot hole in front of the panel to gain enough headroom. I would like to know what was the intent of the code making panel.
(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
I installed a panel under a house with a dirt floor basement using the exception to this article. The ceiling height varied from 6 1/2 feet to 4 feet at different areas. The hot water heater, well pump, furnace, were all installed in this area. The original location of the panel was behind a kitchen cabinet and no longer could be installed in the same location. My options were to install it out doors or in the basement. I choose the basement. The height was about 4 1/2 feet at the edge of the basement wall. I was told by the electrical inspector that it was not the intent of the code to install a panel in this location unless there was already a panel in that spot. I resolved the issue by digging a 2 foot hole in front of the panel to gain enough headroom. I would like to know what was the intent of the code making panel.