110.3(b) question

Status
Not open for further replies.

Sthome25

Member
Location
Coatesville, PA
Occupation
Electrician
Hey guys,

This question is in regards to the coupling being used as a spacer for the minerlac. It is my opinion that 110.3(b) says that a coupling can only be used to connect two pieces of approved conduit together, and therefore, using it as a spacer is a code violation. I was met with overwheliming response that I am wrong and that AHJ can approve this installation. Can you guys clarify this for me? Am I wrong?
 

Attachments

  • coupling question.jpg
    coupling question.jpg
    53 KB · Views: 121

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I think the argument would be the couplings are not used as couplings. The installer could have used some scrap metal instead. It's a stretch to say that if something is trash it cannot be trash because of its listing.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Surprised that response merely overwhelming, I'd have expected more dramatic

That vinyl mounting plate mounted on surface of siding 🤑
Agreed. I think it would have looked better to throw the mounting plate away and just mount it directly to the siding.
Personally I would have complained about that rather then the spacers. The mounting plate is used incorrectly.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I really don't see the need to have the panel set on a flat piece as shown. When you span a bunch of horizontal boards the panel is pretty plumb so why bother.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It is my opinion that 110.3(b) says that a coupling can only be used to connect two pieces of approved conduit together, and therefore, using it as a spacer is a code violation.
Methinks it would be more accurate to say that only a coupling may be used to join two sections of conduit.

It would be difficult to find a rule that actually says that fittings and the like may not be used for any other purpose.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
In my personal opinion, citing this as a violation is just a waste of time. It may be an eye soar but it’s serving a purpose.

I know we all have different opinions and feel differently about certain things.

My biggest thing in being code complaint is safety. There are many situations out there where in the terms of the NEC it is a violation but in terms of safety is fine. Like this for example.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
As far as what is being used as spacers behind the clamps i would think a more aesthetically please option might be available.

The mounting plate as installed just looks to be a hack job.

I question though the clamping device, i don't think it is listed for PVC.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I use a piece of PVC, usually 1/2", (that's about the only thing 1/2" PVC is good for) for a spacer. I have never used a spacer behind a minerlac/cowboy. I usually need them for a 1-hole strap. I won't waste a coupling unless it's all I have. Most times I need it either shorter or longer than a coupling. You can cut the PVC to size.

I agree with the mounting plate being used wrong. It's supposed to be put on before the siding goes up, that's what the slotted flanges are for. And as was mentioned, for retrofit, break off the flanges and slide it behind. Personally, I would omit the siding plate/block and mount straight to the siding.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I see not code issue with using a conduit coupling as a mechanical space. It is the same when I use a length of EMT with back to back caddy clamps as a trapeze support for runs of EMT. It is not EMT at that point...just a metal tube used as a support system.
 

Sthome25

Member
Location
Coatesville, PA
Occupation
Electrician
Well guys based off your responses I guess I am wrong. Its not the first time and it surely will not be the last. Thank you for all the input.

To clarify this picture came from an "electrical wall of shame" groups.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
As far as what is being used as spacers behind the clamps i would think a more aesthetically please option might be available....
Sure, but would that more aesthetically pleasing option be on hand and available in your van, or does it involve a seventy to ninety minute round trip drive to come up with an option that may or may not actually do the job.
 
Status
Not open for further replies.
Top