- Location
- New Jersey
- Occupation
- Journeyman Electrician
Is that really a coupling? The one on the bottom looks like it has the lettering on it that is usually on a piece of PVC raceway which I haven't seen on a coupling.
Yup. On a job last year, I strapped up some 3/4 EMT to some concrete precast and zip tied MC to it. The inspector was a real idiot, he noticed it and said you can't strap cables to raceways. I said that's not a raceway it's just a piece of pipe used to secure and support the MC. He still said I couldn't do it and asked if the EMT was listed for support of mc. I said it didn't have to be, just like using say a 2x4 as a running board the 2x4 is not listed for Cable support. He couldn't come up with a response to that.I see not code issue with using a conduit coupling as a mechanical space. It is the same when I use a length of EMT with back to back caddy clamps as a trapeze support for runs of EMT. It is not EMT at that point...just a metal tube used as a support system.
He should have thought for 2 seconds and realize that the EMT was nothing more than a metal tube being used for support. You 2x4 argument was spot on.Yup. On a job last year, I strapped up some 3/4 EMT to some concrete precast and zip tied MC to it. The inspector was a real idiot, he noticed it and said you can't strap cables to raceways. I said that's not a raceway it's just a piece of pipe used to secure and support the MC. He still said I couldn't do it and asked if the EMT was listed for support of mc. I said it didn't have to be, just like using say a 2x4 as a running board the 2x4 is not listed for Cable support. He couldn't come up with a response to that.
Here an inspector would pick that apart all day long:Hey guys,
This question is in regards to the coupling being used as a spacer for the minerlac. It is my opinion that 110.3(b) says that a coupling can only be used to connect two pieces of approved conduit together, and therefore, using it as a spacer is a code violation. I was met with overwheliming response that I am wrong and that AHJ can approve this installation. Can you guys clarify this for me? Am I wrong?
You are mistaken.Also 110.3(B) specifically refers to equipment, which a coupling is not.
Yeah I don't think that includes couplings, even though it says fittings. It's notable that the list does not include raceways.You are mistaken.
Article 100 Definitions
Equipment - A general term, including fittings, devices, appliances, luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
Fitting - An accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a mechanical rather than an electrical functionYeah I don't think that includes couplings, even though it says fittings. It's notable that the list does not include raceways.
Looks like grey deck screws which are fine for outdoors.Here an inspector would pick that apart all day long:
- The conduit support is sloppy violates 110.12, 300.11(A). A small piece of uni-strut and some strut straps would take 15 min to fix.
- 110.13 the sheetrock screws used are not rated for the environment,
- 110.13 the vinyl 'mounting block' for the meter base does not look secure nor properly flashed.
- SE cable on vinyl siding as service entrance conductors 300.6 and 230.50(B)(1).
- And no LB or bushing where the SE cable turns 300.15(C).
They looked like drywall screws to me. Here an inspector wont approve a #6 screw to secure a meter, deck or drywall.Looks like grey deck screws which are fine for outdoors.
Perhaps but its also very flimsy looking, inspectors here get very nitpickey on service changes.Why would you need flashing around the mounting block the siding is still behind it? It's ugly but there is no violation,
I have yet to see a SE cable service in Washington, Oregon or California.Why can't SE cable be strapped to vinyl siding? Are you saying that the stuff above the meter is subject to physical damage
Except that there are tons of references to 'equipment' throughout the code that are clearly more limited in scope.Fitting - An accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a mechanical rather than an electrical function
I am pretty sure when they say general term the code panel means it all parts used in an electrical system without specifically listing every single item. I find it hard to believe that 110.3(b) would apply to lock nuts, bushings, and the like but couplings would be excluded.
On top of the SE cable connector? Duct seal, not required but very common around here.What's that glob on the top fitting? Water proofing?
Must a NE thing because its used here extensively, not sure how it got started but everyone does it.On top of the SE cable connector? Duct seal, not required but very common around here.
Well it's cheaper, faster, and smaller than a 2" pipe running down the side of the house which makes it less noticeable. When done properly (meaning straight, strapped, and plumb) IMO it looks better than a conduit three times the size.Question?
Why do you guys Run SE like that. Around here its either in the wall or Piped. I would think people hate the look of that. Not criticizing anyone, I don't post pics on here cause I don't want to see were I messed up lol.