Per NEC 110.34(f), "Pipes and ducts foreign to the electrical installation and requiring periodic maintenance or whose malfunction would endanger the operation of the electrical system shall not be located in the vicinity of the service equipment... Protection shall be provided where necessary to avoid damage from condensation leaks and breaks in such foreign systems..." I have a situation in a small commercial building where we may need to bring the fire riser into the building through the electrical room that houses the 400A, 120/208V main service switchboard. There will be no valves, but there will be a flow switch, the rest is just pipe. The pipe does not enter the clear working area above or in front of the board, it is off to the side about 3 feet away.
What qualifies as outside of the "vicinity"? What sort of protection do I need to make this work? Or are these all questions that I should pose to the local inspector as interpretations vary?
Any help would be greatly appreciated.