Energy wise that is true, but the energy savings may not be noticable much over the life of the unit.charlie b said:The simple answer is that there are fewer losses. More of the energy supplied by the power system goes into the room (in the form of cooler air), and less of the energy is lost in the wires (i.e., I^2R losses) or in the inefficiencies of the A/C equipment (e.g., the motor).
But it is not the same as asking, "Which weighs more, a pound of feathers or a pound of gold?" The correct answer to that one is that a pound of feathers outweighs a pound of gold. :smile:winnie said:Asking this is like asking 'Which weighs more, a pound of feathers or a pound of lead?'
charlie b said:But it is not the same as asking, "Which weighs more, a pound of feathers or a pound of gold?" The correct answer to that one is that a pound of feathers outweighs a pound of gold. :smile:
(Really! On the level! :smile: )
Gold is measured in the troy system in which there are 12 troy ounces (each 480 grains) to a troy pound.charlie b said:
But it is not the same as asking, "Which weighs more, a pound of feathers or a pound of gold?" The correct answer to that one is that a pound of feathers outweighs a pound of gold. :smile:
(Really! On the level! :smile: )
brian777 said:The guys at work were all wondering how running a 220v airconditioner or any load for that matter would be cheaper per kilowatt hr than 110v. I know it is I just dont know how to explain it electrically. Can anyone help me on this?
Brian
charlie b said:The simple answer is that there are fewer losses. More of the energy supplied by the power system goes into the room (in the form of cooler air), and less of the energy is lost in the wires (i.e., I^2R losses) or in the inefficiencies of the A/C equipment (e.g., the motor).
Not quite. The system with the higher voltage will have a lower current, and will therefore use a smaller (higher resistance) wire. That part you have correct.iwire said:You lost me, assuming I use larger conductors with the lower voltage the losses would be equal would they not? :-?
I like saying that conductor is more expensive than insulation.drbond24 said:You could say that volts are cheap while amps are expensive.
Let's suppose you wire each of our two hypothetical circuits for the same % of voltage drop; that's the usual measuring stick, right?charlie b said:Thus, with the higher voltage (all else remaining the same), you get a savings of half the I^2R power losses in the wires.
I must admit that I changed my opinion twice, while typing out my reply. Each time I thought it through, I came up with a different opinion. So I had better post this quickly, before I have time to change my opinion again.LarryFine said:Let's suppose you wire each of our two hypothetical circuits for the same % of voltage drop; that's the usual measuring stick, right? How would that affect your conclusion? I think it still works.