Re: 115 volt motor on 208 volt 3 phase control
Charlie,
I think you've given a great reference with 250.6, especially 250.6(A). The grounding conductor will, very likely, be interconnected with other conductive materials (such as building steel, other circuit grounding conductors, exposed conductive surfaces of all manner of equipment that is electrically supplied, as well as any other conductive material(s) in incidental contact with that equipment.
A neutral current, introduced to the grounding conductor web at one point, will take all available paths back to the supply.
Depending upon the specific total assembly of the occupancy's web of grounding conductors and other conductive "noncurrent carrying" material, the return current from this 115 V blower motor will show up all over the facility. . .rather than being contained in an insulated (and inherently isolated) grounded conductor.