11b box stamped says 43.3 CU. IN

Status
Not open for further replies.

PowerMan2020

Member
Location
virginia
Occupation
electrician
Due to splices I need to make, I need a box to be at least 42.5 CU IN and most all of the boxes I see are only 42 cu in.
At home depot the Steel City square 11b's have it stamped saying 43.3 Cu. In., but when I look at the Steel City website and online informational specs they only claim it is 42 cu in. Seems to me if i go by the stamp then I am OK.....any ideas on this discrepancy?


71MF12PW1GL._AC_SL1500_.jpg
 
I would use the box and/or round down without worrying about it.

If it bothers you that much, use a plaster ring and a blank plate to suit.
 
I would use the box and/or round down without worrying about it.

If it bothers you that much, use a plaster ring and a blank plate to suit.

Ugh, I don't have any rings on hand. Perhaps I will use a black marker and circle the stamped volume and possible create a label to stick on the box pointing out that it is a 43.3. Cu. In. I am only afraid that the inspector could just assume it is a 42. cu in box and fail me for being half a cu. in. too small.
 
Ugh, I don't have any rings on hand. Perhaps I will use a black marker and circle the stamped volume and possible create a label to stick on the box pointing out that it is a 43.3. Cu. In. I am only afraid that the inspector could just assume it is a 42. cu in box and fail me for being half a cu. in. too small.

My God, I only wish that was the only thing to keep me awake at night. :rolleyes:

Leave it be. Nobody cares!

-Hal
 
I don't recall an inspector ever, not even once, checking my box fill......
I once had one that did, particuarly paid attention to 1 and 2 gang plastic boxes for NM cable.

I don't generally overfill any box since then, not even by half a conductor, except occasionally on work that won't be inspected and the correct box isn't readily available at the time or would be a big PITA to remove some existing box because it is too small.
 
I have, several times. North Carolina being the worst. I had one inspector pull out all the wires and count. He said if I had one more wire, he would have turned me down! LOL!
Wiring method? Just wondering if he did this at rough in (NM) or at final (conduit system)?

I agree, NC can be a pain at times, but as long as it's code and not opinion I'm okay with it.
 
I have, several times. North Carolina being the worst. I had one inspector pull out all the wires and count. He said if I had one more wire, he would have turned me down! LOL!
Does he put them back, and in a way that rockers won't damage with their roto-zip cutters?
 
Wiring method? Just wondering if he did this at rough in (NM) or at final (conduit system)?

I agree, NC can be a pain at times, but as long as it's code and not opinion I'm okay with it.
Yeah, he was staying with code, but on this particular job, the homeowner had four four ways in one box, entire job #12 minimum. Used the deepest four gang I could find. I passed, but he checked it. Another was City of Roswell many years ago, remodel job, quite a few conduits in one box, but had extension ring on it. Passed on that one too.
 
I do find it interesting that the particular box in question is different then all the others. They must have made it a hair larger in depth perhaps.
 
Maybe it's a "Southern thing".(NC &N TN) . :) I check box fill on every install.. Find 25%+ of the houses wired with #12 and using Carlon 2 gang boxes have a fill problem.
 
In my 3 decades, it only happened once and on the only box, I ever overfilled by one wire. Boy did I chew myself out!
 
They'll check if it "doesn't look right" (we are in the south). The two things that alert them are handy boxes (which I don't use, but I've seen builders put them in overfull. I did have to argue that you can legally get one device and one cable in there once on a retrofit job) and as Augie says, the Carlon boxes with lots of 12g wire hanging out. This is a number that the average inspector can count without removing his shoes and socks.
 
They'll check if it "doesn't look right" (we are in the south). The two things that alert them are handy boxes (which I don't use, but I've seen builders put them in overfull. I did have to argue that you can legally get one device and one cable in there once on a retrofit job) and as Augie says, the Carlon boxes with lots of 12g wire hanging out. This is a number that the average inspector can count without removing his shoes and socks.
Even a 2.125" deep handibox doesn't have room for many conductors if there is a device installed, 1.5" deep are almost useless IMO.
 
Handy-boxes are handy for connections in commercial-kitchen fire-suppression systems, like at the micro-switches and gas valves.

I also like using plastic handy-boxes for the receptacles I install for cabinet-mounted microwave ovens.
 
I was on my job a few years back and was checking the work the guys were doing. I immediately went to 2 boxes that were one over. They had to reroute the circuit to make it work.
 