We have a customer that requires 120/240V for their equipment. Initially 30kVA possibly increasing in the future to 90kVA for a remote celltower. The utility will provide 120/240V service at their closest single phase line which is 12,000’ from the tower location.
We plan to take the 240V service, step it up to 480V, run with multiple sets of 4/0 Aluminum, make use of transformer taps, and install a solid state voltage regulator at the 120/240V equipment location.
We have done our voltage drop calculations and can address that aspect. Our concern is the system operation during transients such as inrush or faults. Has anyone had experience with a long run at 480V?
We plan to take the 240V service, step it up to 480V, run with multiple sets of 4/0 Aluminum, make use of transformer taps, and install a solid state voltage regulator at the 120/240V equipment location.
We have done our voltage drop calculations and can address that aspect. Our concern is the system operation during transients such as inrush or faults. Has anyone had experience with a long run at 480V?