320.10 Uses Permitted.
Where not subject to physical damage, Type AC cable shall be permitted as follows:
(1) In both exposed and concealed work
(2) In cable trays where identified for such use
(3) In dry locations
(4) Embedded in plaster finish on brick or other masonry, except in damp or wet locations
(5) To be run or fished in the air voids of masonry block or tile walls where such walls are not exposed or subject to excessive moisture or dampness
320.12 Uses Not Permitted.
Type AC cable shall not be used as follows:
(1) In theaters and similar locations, except where permitted in 518.4
(2) In motion picture studios
(3) In hazardous (classified) locations except where permitted in
a. 501.4(B), Exception
b. 502.4(B), Exception No. 1
c. 504.20
(4) Where exposed to corrosive fumes or vapors
(5) In storage battery rooms
(6) In hoistways, or on elevators or escalators, except where permitted in 620.21
(7) In commercial garages where prohibited in 511.4 and 511.7