wirenut1980
- Plainfield, IN
Hi everyone, Happy Friday!
I am an engineer at a utility, and we have an unusual situation potentially. All of our padmount transformers are grounded wye-grounded wye. And all of our distribution circuits are grounded wye 12.47/7.2 kV. We have a customer where we may replace some wye-wye padmount transformers with delta-wye padmount transformers. The reason we are considering this is to reduce harmonic current distortion generated by the customer loads. They have 6 pulse VFD's, and also 6 pulse induction furnaces. The strategy is to replace half of the wye-wye transformers with delta-wye transformers. The 30 degree phase shift will help cancel much of the 5th and 7th harmonics. So it would be possible to have some wye-wye transformers, and some delta-wye transformers in an underground loop. The primary concentric neutral at the wye-wye transformers would remain bonded to secondary neutral, and grounded at the transformer.
I am getting questions about what we do with the primary (12.47 kV) concentric neutrals at the delta-wye transformers if we go ahead with this. Do we ground them at the transformer and bond them to the secondary neutral, or do we float them? The secondary neutral will be grounded for 480Y/277 V services at all transformers.
I came across the thread below where someone suggests bonding the primary and secondary neutrals at the delta-wye transformers. My personal feeling is that it could be done this way and any unbalanced load current could return on the primary neutral if the primary and secondary neutrals were bonded together, no harm done.
Or the primary neutral could be floated at the delta-wye transformers, also no harm done, as long as the primary neutral is continuous to accommodate any unbalanced load from the wye-wye transformers.
Is there an advantage one way or the other with respect to what to do with the primary neutral at the delta-wye transformers? Or is there only one correct way to do it?
Thanks in advance!
http://forums.mikeholt.com/showthread.php?t=161313&page=2
Thanks in advance!