ryan_618
Senior Member
- Location
- Salt Lake City, Utah
I have a job that I am inspecting that has a 12,470 volt, ungrounded service. From the utility transformer, they come into the building and immediatly to a service disconnect. After the disconenct is a transfer switch that is attached to a 12,470/7,200 volt, 2.5Mw generator. The generator is impedance grounded. The grounding impedance is 36 Ohms, limitting the fault current to 200 A.
My question: What is the point of having an impedance grounded system with the impedance set so high that it allows 200 amps of fault current??? The 12,470 equipment (after the transfer switch, of course) is all transformers. 12,470 to 4,160 and 12,470 to 480. The circuit breakers for the primary to the 480 transformers will be less than 200 amps.
Any thoughts?
My question: What is the point of having an impedance grounded system with the impedance set so high that it allows 200 amps of fault current??? The 12,470 equipment (after the transfer switch, of course) is all transformers. 12,470 to 4,160 and 12,470 to 480. The circuit breakers for the primary to the 480 transformers will be less than 200 amps.