And what do you bet that the sparky uses a 40 breaker and says a 35 is not standard.
What other wire types would allow #10? Just curious thanks!If you are using NM (romex) cable for that unit it will have to be 8 AWG. With other wiring methods it could be 10 AWG, but not for NM.
Pretty much anything other than NM and UF. So conduit and THHN, MC cable, SE cable would be the most common.What other wire types would allow #10? Just curious thanks!
Just learning here what are the properties of THHN and MC that can handle it at #10 over #8NMB? Is metal clad not NMB with just a metal enclosure?Pretty much anything other than NM and UF. So conduit and THHN, MC cable, SE cable would be the most common.
It is simply a listing requirement in the product standard for NM and a rule in the NEC.Just learning here what are the properties of THHN and MC that can handle it at #10 over #8NMB? Is metal clad not NMB with just a metal enclosure?
See Art. 310 in the NEC.Just learning here what are the properties of THHN and MC that can handle it at #10 over #8NMB?
Definitely not.Is metal clad not NMB with just a metal enclosure?
No, it's identified conductors in a metal sheath.Is metal clad not NMB with just a metal enclosure?
MC cable does not have the 60C limitation that NM-B has. If all your terminations on the entire circuit are listed for 75C heat, then you can use the numbers in the 75C column of Table 310.16. Just make sure and look at the temp rating of the mini split terminations. You always have to figure your ampacity according to lowest temperature rating of any termination on the circuit.Just learning here what are the properties of THHN and MC that can handle it at #10 over #8NMB? Is metal clad not NMB with just a metal enclosure?
But otherwise #8 Romex MNB should work right?MC cable does not have the 60C limitation that NM-B has. If all your terminations on the entire circuit are listed for 75C heat, then you can use the numbers in the 75C column of Table 310.16. Just make sure and look at the temp rating of the mini split terminations. You always have to figure your ampacity according to lowest temperature rating of any termination on the circuit.
Totally understood just trying to learn the trade.Don't go down the path of over-specifying things for the electrician. Yes #8 NMB is a very likely solution in this situation, but that could change based on the specifics of the installation.
Forum rules explicitly prohibit providing DIY help. Since your original question was about confirming that there was a problem for an electrician to fix, we were able to help. But once we start trying to help you fix this directly, the post will get shut down. There are numerous details of an electrical installation, and there is no way that a forum post could anticipate all of the details that we'd assume an electrician knows and you don't even know to ask about.
-Jon
Another thing that makes it more complicated is the "small conductor" rule in 240.4(D). That is where the common assumption that "#14 is 15A, #12 is 20A and #10 is 30A" comes from. That rule does not apply to HVAC installations.Just learning here what are the properties of THHN and MC that can handle it at #10 over #8NMB? Is metal clad not NMB with just a metal enclosure?