I just got a call from a friend and past employee of mine who is working on a very large installation. He is running 12 sets of 400MCM. The job is engineered and the specs called for a 3/0 GEC to the building steel and water pipe.
The inspectors are interpreting 250.66 to mean that 3/0 is the largest GEC if you are using one conductors. They are saying you must use the notes for multiple sets. This is true but what happens when you get beyond the Tables--
I don't think this is correct for one because I can't figure out how you can calculate it.-- 12 x 400000= 4,800,000cm or 4,800MCM. Then what?
Is 3/0 the largest GEC you will ever need?
The inspectors are interpreting 250.66 to mean that 3/0 is the largest GEC if you are using one conductors. They are saying you must use the notes for multiple sets. This is true but what happens when you get beyond the Tables--
I don't think this is correct for one because I can't figure out how you can calculate it.-- 12 x 400000= 4,800,000cm or 4,800MCM. Then what?