Greetings all. I'm trying to clean up an existing lighting installation in the home of a new customer.
There are a total of 14 mono-point-type fixtures, which have had their integral transformers removed and are all powered from a group of three 120Vx12V magnetic transformers (one 0.5 kVA, and two 0.25 kVA). The 0.25 kVA xfmrs. supply 3 fixtures each, and the 0.5 kVA xfmr. supplies the other 8 fixtures.
The problems are many. One certain problem is the 12V wiring: it was done entirely with 12/2 landscape cable (in the attic, and exposed on the open beams of the ceiling). Also, the splices, while sometimes in the wiring compartment of the fixtures, are sometimes in the open.
At least the original installers knew enough to not overload the cables. The six fixtures supplied by the two 0.25 kVA xfmrs. are each fed by a separate 12/2 cable from the wiring compartments of one of those xfmr's. The eight fixtures supplied by the large xfmr. are a bit sketchy: three 12/2 cables run from the xfmr. wiring compartment; two of those cables supply 3 fixtures apiece, and the remaining cable supplies 2 fixtures. The 12/2 cables splice to 16/2 cables to feed the individual fixtures.
All three transformers are supplied by one 1000W dimmer, which of course is NOT LV-rated. The dimmer is easily changed to a magnetic LV type, but there do not appear to be any markings on any of the xfmr's either prohibiting or allowing them to be dimmed.
The transformers are installed in the attic, and have no OCP on the primary (other than the branch CB) and no OCP on the secondary. This brings me to the main questions I have:
Lastly, whether the wiring method was corrected or not, would these fixtures be required to be grounded?
Thanks in advance for reading and responding.
There are a total of 14 mono-point-type fixtures, which have had their integral transformers removed and are all powered from a group of three 120Vx12V magnetic transformers (one 0.5 kVA, and two 0.25 kVA). The 0.25 kVA xfmrs. supply 3 fixtures each, and the 0.5 kVA xfmr. supplies the other 8 fixtures.
The problems are many. One certain problem is the 12V wiring: it was done entirely with 12/2 landscape cable (in the attic, and exposed on the open beams of the ceiling). Also, the splices, while sometimes in the wiring compartment of the fixtures, are sometimes in the open.
At least the original installers knew enough to not overload the cables. The six fixtures supplied by the two 0.25 kVA xfmrs. are each fed by a separate 12/2 cable from the wiring compartments of one of those xfmr's. The eight fixtures supplied by the large xfmr. are a bit sketchy: three 12/2 cables run from the xfmr. wiring compartment; two of those cables supply 3 fixtures apiece, and the remaining cable supplies 2 fixtures. The 12/2 cables splice to 16/2 cables to feed the individual fixtures.
All three transformers are supplied by one 1000W dimmer, which of course is NOT LV-rated. The dimmer is easily changed to a magnetic LV type, but there do not appear to be any markings on any of the xfmr's either prohibiting or allowing them to be dimmed.
The transformers are installed in the attic, and have no OCP on the primary (other than the branch CB) and no OCP on the secondary. This brings me to the main questions I have:
- are these xfmrs. OK to be installed in the attic?
- do they need OCP on the primary and/or secondary?
- If yes to OCP, how to size it, and what best/easiest to use?
- Given the lack of specific info re: dimming, is it safe to dim them with an appropriate dimmer?
Lastly, whether the wiring method was corrected or not, would these fixtures be required to be grounded?
Thanks in advance for reading and responding.