I need to provide a 30 amp receptacle for a trailer that has a 120/240 single phase service. The trailer arrived with a three phase 120/208v five wire receptacle. The owner of the trailer reconfigured the panel in the trailer to accomodate the single phase service, but I am still asking them to change the cord end to a four wire 120/240, as I didn't like the idea of the 208v rated cord being fed by a 240v circuit. In looking into it, I noticed all the standard three phase 5 wire configurations cord/receptacles are 120/208, which makes me wonder if I am being overly cautious. What would one do if they needed to connect a three phase piece of equipment if the service is 120/240 three phase delta? Thanks in advance .