Did you confirm voltage before your work? Maybe noticed A was high leg but didn't look all that close to exactly what the voltage was and it was wrong from the start? Pump you mentioned may run with that condition, and may go for some time if only runs for short cycles and therefore was never noticed before the main breaker failed which prompted the service call.120/208 High leg delta service
4 Wire- 208v[red A]/120v[black B]/120v[black C]/Green[service] and green[ground rod] bonded on N busbar. 1950's farm building.
I go to this service and problems.. the main breaker - not powering the C phase bus bar.
But a 240v/30A drain waste sub is back feeding into the C phase via the actual pump. The lights being powered via pump leg are quite a show.
The panel gets changed out.
During the change out I may have switched B/C phase.
After I put the meter back in the high leg is reading 320v to ground, 420v to phase B, 240 to C.
How can this be? When I pulled the meter there is clear a unacceptable level of corrosion... service conduit is not connect... fittings are just missing... The meter box is scheduled to be changed. But what did I do wrong?
How could I even change the voltage? Maybe I missed the grounding bushing? Corrosion at fault? Meter put in upside down?