To confirm, you're saying I could wire it as 3 phase 208V anyways?Check the nameplate on the motor, there's a good chance it will say Usable At 208V.
No. It is a single phase motor, but a 240 volt motor may be suitable for operation at 208 volts.To confirm, you're saying I could wire it as 3 phase 208V anyways?
No. If the motor says 230V, or 208V-240V on it, it could be powered by 208V/1P from the 208V/3P panel. It may run hotter and slower, however.To confirm, you're saying I could wire it as 3 phase 208V anyways?
That nameplate was not from an OP, it was just an example of how a nameplate marked to indicate that the motor may be run on 208V 2-wire.Says 115/208-230, so you can run it on the 208 you have.
It shouldn't run slower, speed still based on frequency and number of poles in the motor. It will draw more current for same output load than it does if supplied by 240 volts.No. If the motor says 230V, or 208V-240V on it, it could be powered by 208V/1P from the 208V/3P panel. It may run hotter and slower, however.
Depends on the application. In theory it won't slow when just running with no load, but with load the increased slip can cause your motor to slow down, as well as heating up to the point where your windings are damaged. V=I/R, but there are more variables involved than just those.It shouldn't run slower, speed still based on frequency and number of poles in the motor. It will draw more current for same output load than it does if supplied by 240 volts.
V=I*RV=I/R
Yikes, that's an embarrassing typo. Thanks.V=I*R
I suppose depends on the application is true. Most general purpose ~1800 rpm motors are not normally slowing down, they just going to draw more current in order to do the same work. If running them at full output rating that is likely going to shorten life of the motor from the extra heating. If they have a service factor over 1.0 and you are not loading over rating that probably helps some but technically they are still overloaded to some extent.Depends on the application. In theory it won't slow when just running with no load, but with load the increased slip can cause your motor to slow down, as well as heating up to the point where your windings are damaged. V=I/R, but there are more variables involved than just those.
I had a client want to hookup a straight 240V (Meaning nameplate ONLY said 240V) motor to 208V and test to see how it would go before converting a whole facility. The motors held up, but the production line was a few % slower, which caused all kinds of issues with their processes due to the timing of other functions. Ultimately, they decided it was best to replace the 240V motors with 208V-230V/460V to modernize as well as allow for future changes.