120/208V single phase panel amperes

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I can't say I have ever seen a 120/208V single phase panel. Seen a lot of 120/240 Volt single phase panels wired up to 120/208 though.
They are very common for the individual unit feeds in large apartment complexes.
No special equipment is required.
 

Ingenieur

Senior Member
Location
Earth
The sizing math is the same for 120/240 and 120/208
the difference being with 240 the N i is 180 deg opposed and cancels 1:1
ie if both legs balanced then N = 0

With 208 only a 120 deg difference so only cancels (cos 120):1 or 0.5:1
moot since N is full sized
eg 100 A on each leg (phase?) N is 50 A
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...

With 208 only a 120 deg difference so only cancels (cos 120):1 or 0.5:1
moot since N is full sized
eg 100 A on each leg (phase?) N is 50 A
If you have two legs of a 3 phase wye system and 100 amps on each leg, there will also be a 100 amps on the neutral.
The calculation is the square root of the quantity (A² + B² + C²) - ((A)(B) + (B)(C) + (A)(C))
where A = A phase current, B = B phase current and C = C phase current
 

Ingenieur

Senior Member
Location
Earth
If you have two legs of a 3 phase wye system and 100 amps on each leg, there will also be a 100 amps on the neutral.
The calculation is the square root of the quantity (A² + B² + C²) - ((A)(B) + (B)(C) + (A)(C))
where A = A phase current, B = B phase current and C = C phase current

isn't In the phasor sum of the line I's?
I may be wrong
I'll crank it out later
basically Ia ang 0 + Ib ang 120