You can both see my confusion here; I have several senior members saying I do & do not need a buck boost.... a 12% buck boost at 40A is listed at $2800!!!
I think the ones saying you don't need a BB transformer are just saying it is common to connect a 208V motor to 240V. Also, it won't hurt much to connect the heating elements rated for 208V to 240V. It will heat faster but could burn the elements out sooner as has been said.
Although practically speaking, you can connect between the grounded/neutral and the high leg to get somewhere around 208V, it is impracticable for a few reasons:
The voltage probably won't be stable and is not meant to be used that way
You won't find a breaker (without going to a 2 or 3P breaker) that is rated for straight 240V or 208V, they will be slash (/) rated 240/120 or 208/120.
You have to use a breaker that can handle the highest voltage from line to neutral. With your needed voltage, 208V, a (/) slash rated breaker would either be 240/120 or 208/120, the 120 would not be compliant since it is less than the provided 208V high leg to neutral.
So a BB is going to be your best route in this situation.