Technically they are two receptacles that each only accepts the voltage they were designed for, so not interchangeable.I was under the impression that 'dual voltage' receptacles were not quite NEC approved.
I get this from 406.8 Noninterchangability
I was under the impression that 'dual voltage' receptacles were not quite NEC approved.
I get this from 406.8 Noninterchangability
Two voltages on one yoke a problem?
Only if you forget to snap off the terminal tabs.Two voltages on one yoke a problem?
He could use a 3 pole breaker, NO?Two voltages on one yoke a problem?
I don't think it would be needed, but a 2 pole definitely. You could wire like a MWBC but both ungrounded conductors landing on the 240 terminals and the jumper feeding the ungrounded side of the 120 and the grounded conductor landing on the 120 neutral terminal.He could use a 3 pole breaker, NO?
Then they wouldn't have separate circuit on the 240 and 120. Sounds like you are jumping one hot leg.I don't think it would be needed, but a 2 pole definitely. You could wire like a MWBC but both ungrounded conductors landing on the 240 terminals and the jumper feeding the ungrounded side of the 120 and the grounded conductor landing on the 120 neutral terminal.
Never seen one but seems interesting. Not sure of the application.
Don't see it needed but would regardless have to have all circuits disconnected simultaneously. If you were to look at side views of the referenced receptacle it has 3 brass and one silver screws, the one side has 2 brass and a common jumped bridge, and the other side has a brass and silver non bridged terminals one hot one neutral. But if you were to want to have totally seperate Circuits it would have to be handle tied. But kind of would defeat the shortcut this device would give.Then they wouldn't have separate circuit on the 240 and 120. Sounds like you are jumping one hot leg.
Then they wouldn't have separate circuit on the 240 and 120. Sounds like you are jumping one hot leg.
That is exactly how the ones we installed were wired, and what was intended in the design.Then they wouldn't have separate circuit on the 240 and 120. Sounds like you are jumping one hot leg.
>I can see someone bending prongs to fit the topI have taken a 5-20 and twisted the prong to fit a 5-15P.
I can see someone bending prongs to fit the top…![]()
Once, anyway. Or once per receptacle.I have taken a 5-20 and twisted the prong to fit a 5-15P.
I can see someone bending prongs to fit the top…![]()