jumper
- 3 Hr 2 Min from Winged Horses
could this not change pending on the POCO or at the meterbase?
408.3(E) Phase Arrangement. The phase arrangement on
3-phase buses shall be A, B, C from front to back, top to
bottom, or left to right, as viewed from the front of the
switchboard or panelboard. The B phase shall be that phase
having the higher voltage to ground on 3-phase, 4-wire,
delta-connected systems. Other busbar arrangements shall
be permitted for additions to existing installations and shall
be marked.
Exception: Equipment within the same single section or
multisection switchboard or panelboard as the meter on
3-phase, 4-wire, delta-connected systems shall be permitted
to have the same phase configuration as the metering
equipment.
FPN: See 110.15 for requirements on marking the busbar
or phase conductor having the higher voltage to ground
where supplied from a 4-wire, delta-connected system.