As stated in post #3, it is a 120/208Y volt panel fed from a 208Y/120 volt system; per IEEE C84.1 Table 1 Note (d).
It would not be a Y system to a single phase sub panel.
You cant have a Y if you don't have all 3 legs.
JAP>
As stated in post #3, it is a 120/208Y volt panel fed from a 208Y/120 volt system; per IEEE C84.1 Table 1 Note (d).
Maybe it should be called a V system to the subpanel.
JAP>
You can argue or disagree all you'd like, it will not change what the standard says.
Perhaps you should contact IEEE standards committee and formulate your argument with them.
Cheers~
Seems to be par for the course here..............No need to confuse or convolute a simple issue.
JAP>
Seems to be par for the course here..............
That would make some sense.Maybe it should be called a V system to the subpanel.
JAP>
If labeled or plans are marked "120/208 single phase" - I will take that to mean two phase conductors and the neutral of a wye system. Only "usual" way to have both those voltages between just three conductors is via a wye connected source, or an inverter that is simulating wye output.So what do you properly call voltages that feed 120/208v 1ph panels that are fed from a 120/208v Y 3ph panel?
JAP>
If labeled or plans are marked "120/208 single phase" - I will take that to mean two phase conductors and the neutral of a wye system. Only "usual" way to have both those voltages between just three conductors is via a wye connected source, or an inverter that is simulating wye output.
And that's the crux....not one but two.If labeled or plans are marked "120/208 single phase" - I will take that to mean two phase conductors and the neutral of a wye system.
I completely agree, but, as indicated in post #40, it's magically a 120/208Y volt subpanel fed from a 208Y/120 volt system; per IEEE C84.1 Table 1 Note (d).
I'm still trying to figure out how you can feed a subpanel single phase 120/208 volt from a 208Y/120 volt system and it still be considered a Y at the subpanel with only 2 phase conductors and 1 neutral.
I'm being sarcastic of course.
JAP>
FWIW you still can derive three phase from it with an open delta primary connected transformer.I completely agree, but, as indicated in post #40, it's magically a 120/208Y volt subpanel fed from a 208Y/120 volt system; per IEEE C84.1 Table 1 Note (d).
I'm still trying to figure out how you can feed a subpanel single phase 120/208 volt from a 208Y/120 volt system and it still be considered a Y at the subpanel with only 2 phase conductors and 1 neutral.
I'm being sarcastic of course.
JAP>
It is still a Y system at the source. I don't see how it is still not part of that service or system just becasue you did not run all 4 wires.
FWIW you still can derive three phase from it with an open delta primary connected transformer.
Oops,said that wrong - open delta secondary
Correct. Just two.Leave the transformer out of it.
There is not 3 phases at the subpanel.
JAP>
I never said there was, I said you can derive three phase from this panel. Can't do that from same panel if it is supplied by 120/240 three wire supply. More common to see it done from medium voltage distribution lines, but concepts are still the same.Leave the transformer out of it.
There is not 3 phases at the subpanel.
JAP>
Because L1-N is single phase, L2-N is single phase, and L1-L2 is single phase.And that's the crux....not one but two.
No matter what you call it.
L1 to N is not in phase with L2 to N.
How can that really be single phase no matter what you call it?
You can not directly run a three phase load from it, though as I earlier mentioned you can derive an open delta system from it from which you can directly run a three phase load.And that's the crux....not one but two.
No matter what you call it.
L1 to N is not in phase with L2 to N.
How can that really be single phase no matter what you call it?