Can I have a 120/240 volt, 3 phase panel (high phase leg) and connect (10) ten 5KW, single phase electrical wall heaters utilizing all three phases.
So, the first wall heater will be connected to AB leg, the second wall heater connected to BC, the thrid wall heater connected to CA leg and so on..
I also have a sub-feed 120/240 volt single panel that services lighting and receptacles connected to AC legs (non-high legs), which the loads is 6KW.
Is the following panel size calcualtion correct?
10 X 5KW wall heaters = 50KW divided by 240V three phase =120.4 amps
6KW lighting / receptacles = 6KW divided by 240V single phase = 25 amps
So, the total panel amps is (120.4 amps + 25 amps) =145.4 amps. I would install a 200A, 120/240V three phase panel with a 200A three pole main circuit breaker.
Is this correct??
Thanks
Is this correct??