120/240 volt receptacle?

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Am I missing something? What is the need for a 2 pole and a single pole breaker? One 2 pole or two single poles with a handle tie should be all that is needed.
Dave, the receptacle shown would need a two pole breaker and a single pole breaker, (or one three pole) but even with that being the case handle ties (or tie) could be used.


Roger
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
. Here is a pic.

41QpAiSUMwL._SL500_AA300_.jpg

That's a Leviton sold on Amazon.
In reference to the image- two ungrounded, separate phases on the top screws; one grounded on the right side, bottom and everything should check out line to line and line to ground.
 

kwired

Electron manager
Location
NE Nebraska
You can buy handle ties by the bag.

I am sure the ability to do this depends on the manufacturer of the breakers in question.

Take QO breakers for example. There is only a single handle on multipole breakers, I don't believe they have a listed handle tie for use on three separate poles, you may be able to use a handle tie between a single and two pole breaker - but I don't know they are intended or listed for such application. I have to admit I mostly use QO breakers and am not as familiar with accessories for other brands out there, so part of my answer is based on what I know about QO breakers, and what accessories are available for them.

I also really don't know that the listing for any other two pole breakers that are available are intended to remove the tie between the individual poles. Maybe you can, but I just wanted to bring that up.

Another interesting question is would it be acceptable to supply this receptacle with a three pole breaker installed in a single phase panel? It will work, but is the three pole breaker listed, or otherwise allowed for this installation?
 

fmtjfw

Senior Member
Design wise, yes. I would prefer to have the receptacles on seperate circuits so tripping the OCPD for one would not affect the other......but......

I would have to look, but I don't the the NEC would allow that, since there is a common yoke involved.

Asked for separate 240V and 120V circuits, three poles needed. that's why 1 1-pole and 1 2-pole
 