I work for an international NGO as an electrician.
We are building a small hospital in Haiti. The city power to the site is 120/240 single phase. Its the same thing you would see at 99.5% of any residential service in the US. There is NO 3 phase equipment. We will of course need back up power.
We are having a difficult time finding a 65 kva 120/240 volt single phase generator. It is much easier to source a 208/120 volt 3 phase generator. We have been discussing this as a work around.
I would use 3 phase panels in the hospital.
We use 4 pole transfer switches. On the city power side of the transfer switch you would jump L2 - L3 to power the missing phase. There is no three phase equipment.
When purchasing equipment for the hospital we would make sure that it is dual rated for 208 volts and 240 volts.
1: Are there any huge safety issues with doing this? I would of course still balance the loads on the city power L1 and L2.
2: Are 3 phase generators more efficient than single phase generators as far fuel consumption.
3. How bad is it to run a 3 phase generator on single phase? I am assuming it would cause lots of vibration and stress on the fly wheel.
We are building a small hospital in Haiti. The city power to the site is 120/240 single phase. Its the same thing you would see at 99.5% of any residential service in the US. There is NO 3 phase equipment. We will of course need back up power.
We are having a difficult time finding a 65 kva 120/240 volt single phase generator. It is much easier to source a 208/120 volt 3 phase generator. We have been discussing this as a work around.
I would use 3 phase panels in the hospital.
We use 4 pole transfer switches. On the city power side of the transfer switch you would jump L2 - L3 to power the missing phase. There is no three phase equipment.
When purchasing equipment for the hospital we would make sure that it is dual rated for 208 volts and 240 volts.
1: Are there any huge safety issues with doing this? I would of course still balance the loads on the city power L1 and L2.
2: Are 3 phase generators more efficient than single phase generators as far fuel consumption.
3. How bad is it to run a 3 phase generator on single phase? I am assuming it would cause lots of vibration and stress on the fly wheel.