Volt-Amps
Member
- Location
- Indianapolis
The utility engineer said we will be getting our 3 phase power from a pole with 3 transformers. The service will be 120/240V, 3 phase. I asked if it's a high leg, he said closed delta and open delta are different, there is no high leg in a closed delta system and connecting to phase B is no problem.
Maybe I am doing too much reading on the internet because of the conflicting information I am getting. Could the experts please help with the following questions:
I appreciate all the help.
Maybe I am doing too much reading on the internet because of the conflicting information I am getting. Could the experts please help with the following questions:
- Would a 120/240V, 3 Phase closed delta service be a 3-phase, 4 wire or 3 phase, 3 wire? Would there be a neutral coming from utility?
- Would a 120/240V, 3 phase, closed delta service from utility have a high leg?
- If no high leg, does this mean on I can distribute loads anyway I want in my panel schedule without concern regarding phase B?
- If there is a high leg, is it similar to open delta with two transformers on the pole where phase B can't be used for 120V circuits?
I appreciate all the help.