Volt-Amps
- Indianapolis
Regards,
To my knowledge, we will always have a high leg with open or closed delta 3-phase 120/240V distribution. The designer at ComEd, the power utility company in Chicago, said they are not the same, and that we can use A, B and C legs just like 120/208, 3-phase. I'm worried if I populate the schedule this way and issue to the contractor, someone would be calling me in the middle of the night about a fire somewhere
. With open delta, we can't use the B phase for 120V, or 240V, 1-PH loads (please correct me if I'm wrong. How does the closed delta differ? there is a 208V in a closed delta between C and the neutral (or B and the neutral, not sure). is it usable? it's like a 1-pole breaker with hot and neutral connections that is a 208V breaker. is this correct? can I use it? and if I can,208V equipment usually have 2 points of connections to connect 2 hots and a ground, how do I feed it from a 1-pole breaker rated at 208V?
I guess there are multiple questions in this post, I hope I'm not confusing anybody, but based on the above, this is what it comes down to:
A-B phase: Can I connect 120V and 240V, 1-Phase here?
B-C phase: Can I connect 120V and 240V, 1-Phase here?
A-C phase: Can I connect 120V and 240V, 1-Phase here?
And the second question is, is there such an thing as a 1-pole, 208V breaker that can power 1-Phase, 208V piece of equipment (hot, neutral and ground).
Finally, what can I not do circuiting-wise on a 3-Phase, 4-Wire closed delta system with high leg?
Thanks
Thanks