Sierrasparky
- USA
- Electrician ,contractor
Silly should be a clue that you're not quite thinking right :slaphead:
Not saying it don't happen... but I am saying rarely.
Base upsizing on the minimum EGC size. 2/0 AL EGC for a 200A OCPD is substantially oversized. The 4/0's would have to be six sizes oversized for the OCP before upsizing the EGC comes into play (in the neighborhood of a 40A OCPD).
It's silly because you need to read 250.112 Nowhere does it indicate a starting point or base on a table. It just says
"shall be increased in size proportionately according to the circular mil area of the ungrounded conductors"