Panel A still has 200A from the utility and 64A of continuous inverter output connected to it. So for 705.12(B)(1) it would need a bus of at least 200A + 1.25 * 64A = 280A (not likely). For 705.12(B)(2), you'd need to move the feed thru lug kit to the bottom to be next to the 32A of inverter output directly connected to panel A; then the busbar rating would only need to be 280A / 120% = 233A (still not likely).Ahh then what about a more complex scenario, they have two 32A inverters one in each panel and a lug kit in the center of panel A?
It could in theory comply with 2023 NEC 705.12(B)(3), either the as-written version that just looks at breakers in Panel A, or the as-it-should-be-written version that would look at all breakers in Panel A and Panel A1.That wouldn't comply with 705.12(B)(1), (2), or (3).
Ok it could possibly comply with the as-written version, correct. It wouldn't comply with the as-it-should-be-written version with the 200A breaker shown in Panel A1; the sum is already too great even without knowing the other breaker ratings.It could in theory comply with 2023 NEC 705.12(B)(3), either the as-written version that just looks at breakers in Panel A, or the as-it-should-be-written version that would look at all breakers in Panel A and Panel A1.
Cheers, Wayne
Agreed. Even if it would comply with some interpretation of the letter of the NEC it would be exploiting a loophole to get around the intent of the code. I don't do loopholes.Ok it could possibly comply with the as-written version, correct. It wouldn't comply with the as-it-should-be-written version with the 200A breaker shown in Panel A1; the sum is already too great even without knowing the other breaker ratings.
My "as-it-should-be-written" version of 2023 NEC 705.12(B)(3) would allow as an option, for the case of side by side panelboards, looking beyond the 200A main breaker in Panel A1 to instead count all the breakers in Panel A1. So then it could be satisfied. Although it wouldn't be likely, as why have two side by side panelboards if the sum of all the relevant breakers in both is less than 200A?It wouldn't comply with the as-it-should-be-written version with the 200A breaker shown in Panel A1; the sum is already too great even without knowing the other breaker ratings.
Difficult or not, I have had to do that.For distant panelboards, even though the same electrical logic would apply, as an enforcement/practical matters, the labeling and verification of compliance would just be too difficult to be practical.
For what rules? I was talking about a hypothetical version of 2023 NEC 705.12(B)(3) that would require labeling two panels connected as in post 21 each something like "sum of all breakers in this panel and that panel 50' over there, excluding the breakers protecting the busses, may not exceed 200A."Difficult or not, I have had to do that.
I did it for PV system interconnections with taps on the load side of existing beakers that were feeding remote MLO subpanels. I designed them with OCPD on the load sides of the taps. Is that what you were talking about?For what rules? I was talking about a hypothetical version of 2023 NEC 705.12(B)(3) that would require labeling two panels connected as in post 21 each something like "sum of all breakers in this panel and that panel 50' over there, excluding the breakers protecting the busses, may not exceed 200A."
Cheers, Wayne
Rube Goldberg called; he wants his machine back.Here is another one that I think meets the letter of the 2023 code:
View attachment 2571353
Here is another one that I think meets the letter of the 2023 code;
No, that just uses the feeder interconnection rules and is a great option in general. I was talking about a hypothetical version of the "sum of all breakers" rule that looks across two panelboards interconnected via feed thru lugs.I did it for PV system interconnections with taps on the load side of existing beakers that were feeding remote MLO subpanels. I designed them with OCPD on the load sides of the taps. Is that what you were talking about?
Yeah I am just thinking of all the cases 705.12(B) does not address in the 2023.Nope, that one also has 64A of inverter output connected to Panel A. So the same considerations as to the schematic in post 21 would apply. Although as the inverter output is already at the opposite end of the bus as the primary supply to Panel A, using the 120% rule would be easier, if you could get a bus rated 233A. More likely, get a bus rated 225A and use a 175A MB in Panel A.
Cheers, Wayne
I don't see the other rules as being ambiguous in the presence of feed-thru lugs. (1) ignores them, they are immaterial. For (2), if they are at the end of the bus opposite the primary supply, then you just can't use (2). And (3) ignores them, which is a mistake but how it's written. (3) needs an internal limitation with respect to feed-thru lugs.
So we have a few imperfect interpretations of (5):
(A) It's attempting to modify (1), (2) and (3); if you have subfeed lugs, you must satisfy (5) before you can use (1), (2), or (3). But the text at the beginning of 705.12(B) is not written in a way that allows (5) to modify (1), (2), and (3).
(B) It's providing an additional allowance not present in (1), (2), or (3), but does so only implicitly.
(C) It's useless text that does nothing.
I'm arguing for (B); I guess you're arguing for (A) or (C)?
Note that if in (2) the subfeed lugs aren't at the end of the bus, they are immaterial to compliance with (2). So the only additional allowance that (5) can offer with respect to (2) is to allow the subfeed lugs at the end of the bus and allow connecting of the secondary source at the penultimate connection.
Note further that (2) could be modified in general to permit one load (OCPD limited) connection between the secondary source connection and the end of the bus, without any risk of overloading the bus. Or maybe with most bus layouts, as there are two bottom most positions, each such position will connect the very bottom of the bus for one pole, and the second pole (and third pole) would already be not quite farthest?
Cheers, Wayne
I agree the intent is to modify (1), (2), and (3), but the first paragraph of 705.12(B) isn't phrased in a way that makes that possible. Each subitem needs to be independent. So (1), (2) and (3) would need language precluding their use when there are feed-thru lugs, unless (5) is complied with.I just read the section again, and again, and again, and maybe even a few more times... and I think it is (A).
Here is another one that I think meets the letter of the 2023 code:
View attachment 2571354
I completely agree!I agree the intent is to modify (1), (2), and (3), but the first paragraph of 705.12(B) isn't phrased in a way that makes that possible. Each subitem needs to be independent. So (1), (2) and (3) would need language precluding their use when there are feed-thru lugs, unless (5) is complied with.
Cheers, Wayne
I agree the intent is to modify (1), (2), and (3), but the first paragraph of 705.12(B) isn't phrased in a way that makes that possible. Each subitem needs to be independent. So (1), (2) and (3) would need language precluding their use when there are feed-thru lugs, unless (5) is complied with.