120 v circuit in a 240 v 3 phase panel, no neutral

Status
Not open for further replies.
Are you even sure that it's a 4W Delta service with a "center tapped", grounded winding? Seems strange they wouldn't run a neutral. If it doesn't have a center tapped 240/120 transformer in the bank, you'll have to get a neutral wired at the transformer bank. That may involve the POCO. If it's a corner grounded Delta, you've got even bigger problems. Maybe I just didn't understand all of the posts, so if my comments are stupid, forget it....I won't be offended (much).
 
Last edited:
Are you even sure that it's a 4W Delta service with a "center tapped", grounded winding? Seems strange they wouldn't run a neutral. If it doesn't have a center tapped 240/120 transformer in the bank, you'll have to get a neutral wired at the transformer bank. That may involve the POCO. If it's a corner grounded Delta, you've got even bigger problems. Maybe I just didn't understand all of the posts, so if my comments are stupid, forget it....I won't be offended (much).
It was a sub panel within the building - service is very likely to have a neutral supplying it. That sub panel probably had no need for a neutral when it was installed, or could even originally been a branch circuit that didn't need a neutral that someone made into a feeder at some point.

I've seen ball field lighting where they never ran neutrals to the light poles - no need to as the lighting was 240 volts. Then someone involved with the operations wants a 120 volt receptacle on a pole for some reason - A good electrician tells them it will cost more then a breaker and a receptacle, so they hire a handyman or do it themselves and you end up with neutral current on the EGC.
 
Number one rule

Number one rule

The number one rule in electrical work. positively identify what you are working on. ( should be/ most likely/probably) will get YOU in trouble.
 