We have a customer that has 5 display computers and monitors for displaying process information in a new control room being built. We had initially planned a home run circuit for each computer / monitor combo with small ups to protect each one so 5 small ups units.
Now the customer wants all 5 outlets wired to the ups and not the breaker panel and use the larger ups in their server rack in the adjacent room to power them. This is all raised floor and MC cable but most of the wall outlets are run through the studs with MC back to the breaker panel.
The load is no problem because the ups are sized 400% over what's needed for the rack it's supplying. I don't think this is a code violation but not 100% sure.
If it's not a code violation do these outlet covers have to a different color or something to indicate they are fed from a UPS and not from a circuit directly in the breaker panel.
The large UPS in the server rack is fed by a 230 VAC circuit.