120 VAC Wall receptacles fed from UPS

Status
Not open for further replies.

tganz96

Member
Location
Dallas , Texas
We have a customer that has 5 display computers and monitors for displaying process information in a new control room being built. We had initially planned a home run circuit for each computer / monitor combo with small ups to protect each one so 5 small ups units.

Now the customer wants all 5 outlets wired to the ups and not the breaker panel and use the larger ups in their server rack in the adjacent room to power them. This is all raised floor and MC cable but most of the wall outlets are run through the studs with MC back to the breaker panel.

The load is no problem because the ups are sized 400% over what's needed for the rack it's supplying. I don't think this is a code violation but not 100% sure.

If it's not a code violation do these outlet covers have to a different color or something to indicate they are fed from a UPS and not from a circuit directly in the breaker panel.

The large UPS in the server rack is fed by a 230 VAC circuit.
 
Will you still have 15 or 20 amp receptacles and 15 or 20 amp conductors protected by 15 or 20 amp overcurrent devices?
 
CVS does something similar, they have a small ups that a cord and plug from the wall feeds several receptacles in the pharmacy area. Kinda sketchy way to do it, but it’s what their engineers want.
 
Wouldn't the plug and cord connection to the load side of the UPS be like the problem with cord and plug lights being permanently mounted. It would require tools to install and remove
 
Although commonly done, is the cord from UPS outlet to building wiring inlet allowed per NEC?

Why not just use an inlet installed in the wall by the UPS. Then a short male/female cord from the UPS to the inlet. I don't think anybody could argue with that.

And I would make the UPS powered receptacles red or blue.

-Hal
 
Why not just use an inlet installed in the wall by the UPS. Then a short male/female cord from the UPS to the inlet. I don't think anybody could argue with that.

And I would make the UPS powered receptacles red or blue.

-Hal
It would be a much cleaner look, and not look like something was rigged up.
 
Will you still have 15 or 20 amp receptacles and 15 or 20 amp conductors protected by 15 or 20 amp overcurrent devices?
So it would be standard receptacles with 12 AWG wire but fed from the ups so it has no protection per outlet but only protection for a group of outlets.
 
So it would be standard receptacles with 12 AWG wire but fed from the ups so it has no protection per outlet but only protection for a group of outlets.
Something mentioned that I initially wasn't thinking about is portable type UPS that would plug in and have receptacles on the unit could be scrutinized by art 400 as to whether you can use the flexible cord as permanent wiring. Outside of that I don't see any problems. This server rack UPS that is supplied by 240 volts may not be that type of unit? Listing instructions maybe next thing to consider, can it supply receptacles not part of the rack?
 