1200 amp rating and clearances, does the setting of the OCP change things?

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
The installation is a 1,200 amp rated switch gear, a 1,200 amp frame main breaker, the setting on the main is less than 1,200 amps. Does this change the requirements for the electrical room, like fire rating?
 
.. the setting on the main is less than 1,200 amps. Does this change the requirements for the electrical room...
The less than 1200A setting does not change the 1200A equipment rating. So your room has to be compliant with 110.26(C)(2) if the gear is over 6' wide
 