I did an inspection on a 3 phase 208V 1200 amp service.
Three riser conduits, with four 600 kcmill conductors, from the CT to the overhead drop.
From the CT to the 1200 amp main breaker, the contractor ran three sets, of four 500 kcmill conductors.
My first thought was a violation of 240.4 (B).
After thinking about it, if this was a switch gear, with six or less switches, without a single main switch, wouldn't load calculation dictate the conductor size.
edit to add, I have to run out check back later, Thanks.