I have a 480VAC 1200A 3PH fused feeder to a 600V Class MCC. The MCC is used to feed 2, 250HP motors, which both are coupled via belts to the shaft of a common arbor. One of the motors starts via soft start. The other which starts across the line, is delayed to start via PLC timer for 2 seconds. The locked rotor current of either motor is enough to blow the 1200A main fuses if the arbor is in a bind. Total running load is well under FLA. The total load on the MCC is not much past the 2 - 250HP motor loads, 3 - 5HP motor loads and a small lighting load.
A fuse blows nearly once a week, and I might mention are expensive. I believe everything calculates in NEC spec. The main could have been bigger to prevent this issue, but I think the company just took the bigger motor upgrade.
All motors and loads have been megged, finding no shorts.
Other than a binding arbor, I can suggest no other reason why the fuse is blowing. Any thoughts would be a help thanks in advance.
A fuse blows nearly once a week, and I might mention are expensive. I believe everything calculates in NEC spec. The main could have been bigger to prevent this issue, but I think the company just took the bigger motor upgrade.
All motors and loads have been megged, finding no shorts.
Other than a binding arbor, I can suggest no other reason why the fuse is blowing. Any thoughts would be a help thanks in advance.