I need to size the grounded conductor between the 480V side of a utility transformer and the customer's service entrance equipment (1200A breaker) on a 750kW PV system (only PV, no significant loads).
I've been told that this should be treated as a feeder with a 1200A overcurrent protection due to the PV inverters (w/ 3/o EGC and 3/o neutral) per 250.122. However, it also seems to fit under a service entrance sizing from 250.66 which would put the grounded conductor at a 1/o (600kcmil per conduit).
Should this be treated as a service entrance or a feeder?
I've been told that this should be treated as a feeder with a 1200A overcurrent protection due to the PV inverters (w/ 3/o EGC and 3/o neutral) per 250.122. However, it also seems to fit under a service entrance sizing from 250.66 which would put the grounded conductor at a 1/o (600kcmil per conduit).
Should this be treated as a service entrance or a feeder?